The problem with limitation swich configuration
yethsts
Post by yethsts » Fri Jul 31, 2020 12:46 am
I find if I configured the ch->LimitSwitchOptions=0x12f in th initializer thread , when the motor stop at end of the initializer c program, the "feed hold" status is activated, and then the g code (such as your example program named "DynoMotion.ngc") wouldn't run. But if I configured the LimitSwitchOptions=0x00 in the initial thread, the g code program can run. But it is dangerrous because there is no limit position detection. Why?
Your ch->LimitSwitchOptions if very strange and easily make the whole system stop and cann't rework.
Re: The problem with limitation swich configuration
Post by TomKerekes » Fri Jul 31, 2020 5:20 pm
Hi yethsts,
You might be setting the wrong polarity for your Limit Switch Inputs. What state are the inputs when activated (touching limit)?
To use the opposite polarity configure: ch->LimitSwitchOptions=0x123
yethsts
Post by yethsts » Sat Aug 01, 2020 4:06 am
Yes, I am wrong. I configured the CH->LimitSwitchPosBit=0x00. Now I changed the 0x00 to the correct IO number, so the problem is solved.
But I have a new problem: In the end of initialization, I call the c function named zero() to reset the tool position (I guess). After it the number in axis window of kmotion be zero. And I can jog the all XYZ motors using the CNC's JOG button. But if I run the second line of your example gcode named "DynoMotion.ngc", the line is:G00 X-37.939 Y8.793 Z16.000 . It always report error: "soft limit Y+ rapid tranverse job halted". I have tried to change the Y8.793 to Y0 or Y-8.793, or change the ch->SoftLimitPos and ch->SoftLimitNeg to very big value such as: 1e+030 and -1e+030, but always the error happen. Why? (The first line of the DynoMotion.ngc is : G90 G21. I also selected/checked the "Machine Coord" and use the "abs coordinate" in CNC window.)
Sincerely,
Huang
yethsts
Post by yethsts » Sat Aug 01, 2020 4:09 am
And I also found if I change the first line code to G91 G21, then the next line of the gcode program can run.
Post by TomKerekes » Sat Aug 01, 2020 4:23 pm
Hi Huang,
What are your KMotionCNC | Tool Setup | Trajectory Planner | Axis Parameters | Cnts/inch ? A zero will cause a division by zero when machine counts to inches.
Otherwise please post your Initialization C Program and your KMotionCNC Tool Setup settings.
yethsts
Post by yethsts » Sat Aug 01, 2020 5:11 pm
Sorry, there was a mistake in my yesterday's description. The fact is: if I use a very large number such as +-7e+6 for the SoftLimitPos and SoftLimitNeg, the g code can run. But if I use a smaller number such as +7e+5 for the SoftLimitPos and -7e+5 for the Neg, the system will output the error I yesterday said.
Post by TomKerekes » Sat Aug 01, 2020 6:05 pm
Please post your Initialization C Program and your KMotionCNC Tool Setup settings.
yethsts
This is the init program. I have commented the zero() part, but the error still appeared.
Post by yethsts » Sat Aug 01, 2020 8:22 pm
#define Lim0 183 // 我自己外加的测试用限位开关编号,接到kFlop板的通道0
#define Lim1 173 // 通道1接入的限位开关对应的IO编号
#define Lim2 172 // 通道2接入的限位开关对应的IO编号
#define Lim3 171 // 通道3接入的限位开关对应的IO编号
#define Lim4 168 // 通道4接入的限位开关对应的IO编号
#define Lim5 169 // 通道5接入的限位开关对应的IO编号
#define Lim6 170 // 通道6接入的限位开关对应的IO编号
// #define Lim7 // 目前未接,通道7接入的限位开关对应的IO编号
#define OutputCh0 8
#define OutputCh1 9
#define OutputCh2 10
#define OutputCh3 11
#define OutputCh4 12
#define OutputCh5 13
#define OutputCh6 14
#define OutputCh7 15
#define Relay1 29 // 控制通道0,1外接的闸
#define Relay2 30 // 控制通道2 外接的闸,控制x轴电机
#define Relay3 31 // 控制通道4,5外接的闸,控制y轴电机
#define Relay4 32 // 控制通道3,6外接的闸,控制z轴电机
#define StopWhenLow_Mode 0x10f
#define DisallowDriveIntoLimit_Mode 0x11f
#define StopMovement_Mode 0x12f
#define ESTOP 26 //红色停止按钮
#define Velocity 40000
#define SPEED 15000 // 移动速度
#define XAxis 2 // x轴对应的通道编号
#define YMasAxis 4 // y主轴对应的通道编号
#define YSlaAxis 5 // y从轴对应的通道编号
#define ZMasAxis 3 // z轴对应的通道编号
#define ZSlaAxis 6 // // z从轴对应的通道编号
#define Test_CH ch0
#define XAxis_CH ch2
#define YAxis_MASTER_CH ch4 //Y主轴通道名称
#define YAxis_SLAVE_CH ch5 //Y从轴通道名称
#define ZAxis_MASTER_CH ch3 //Z主轴通道名称
#define ZAxis_SLAVE_CH ch6 //Z从轴通道名称
#define X_Lim Lim2 // ch2
#define YMas_Lim Lim4 //ch4
#define YSla_Lim Lim5 //ch5
#define ZMas_Lim Lim3 //ch3
#define ZSla_Lim Lim6 //ch6
#define X_Relay Relay2 //ch2
#define Y_Relay Relay3 //ch4,ch5
#define Z_Relay Relay4 //ch3,ch6
#define X_OutputCh OutputCh2 //ch2
#define YMas_OutputCh OutputCh4 //ch4
#define YSla_OutputCh OutputCh5 //ch5
#define ZMas_OutputCh OutputCh3 //ch3
#define ZSla_OutputCh OutputCh6 //ch6
#define LimActOption StopMovement_Mode
SetBit(UseRelay); // 抱闸,NPN三极管导通,继电器线圈得电,常闭触点断开,闸及限位开关供电0v,抱闸
ClearBit(UseRelay); // 松闸,NPN三极管截止,继电器线圈失点,常闭触点闭合,松闸,闸及限位开关供电24v
double T0, LastX = 0, LastY = 0, LastZ = 0, LastA = 0, Tau;
KStepPresent = TRUE; // enable KSTEP input multiplexing
FPGA(STEP_PULSE_LENGTH_ADD) = 63 + 0x80; // set polarity and pulse length to 4us
////////////////////////// X axis configuration //////////////////////////////////////////////
XAxis_CH->InputMode = NO_INPUT_MODE;
XAxis_CH->OutputMode = STEP_DIR_MODE;
XAxis_CH->Vel = Velocity;
XAxis_CH->Accel = 200000;
XAxis_CH->Jerk = 4e+006;
XAxis_CH->P = 0;
XAxis_CH->I = 0.01;
XAxis_CH->D = 0;
XAxis_CH->FFAccel = 0;
XAxis_CH->FFVel = 0;
XAxis_CH->MaxI = 200;
XAxis_CH->MaxErr = 1e+006;
XAxis_CH->MaxOutput = 200;
XAxis_CH->DeadBandGain = 1;
XAxis_CH->DeadBandRange = 0;
XAxis_CH->InputChan0 = 0;
XAxis_CH->InputChan1 = 0;
XAxis_CH->OutputChan0 = X_OutputCh; //
XAxis_CH->OutputChan1 = 0;
XAxis_CH->MasterAxis = -1;
//XAxis_CH->LimitSwitchOptions=0x0;
XAxis_CH->LimitSwitchOptions = 0x00; //
XAxis_CH->LimitSwitchNegBit = X_Lim;
XAxis_CH->LimitSwitchPosBit = X_Lim;
XAxis_CH->SoftLimitPos = 1e+009;
XAxis_CH->SoftLimitNeg = -1e+009;
XAxis_CH->InputGain0 = 1;
XAxis_CH->InputGain1 = 1;
XAxis_CH->InputOffset0 = 0;
XAxis_CH->InputOffset1 = 0;
XAxis_CH->OutputGain = 1;
XAxis_CH->OutputOffset = 0;
XAxis_CH->SlaveGain = 1;
XAxis_CH->BacklashMode = BACKLASH_OFF;
XAxis_CH->BacklashAmount = 0;
XAxis_CH->BacklashRate = 0;
XAxis_CH->invDistPerCycle = 1;
XAxis_CH->Lead = 0;
XAxis_CH->MaxFollowingError = 1000000000;
XAxis_CH->StepperAmplitude = 20;
XAxis_CH->iir[0].B0 = 1;
XAxis_CH->iir[0].B1 = 0;
XAxis_CH->iir[0].B2 = 0;
XAxis_CH->iir[0].A1 = 0;
XAxis_CH->iir[0].A2 = 0;
XAxis_CH->iir[1].B0 = 1;
XAxis_CH->iir[1].B1 = 0;
XAxis_CH->iir[1].B2 = 0;
XAxis_CH->iir[1].A1 = 0;
XAxis_CH->iir[1].A2 = 0;
XAxis_CH->iir[2].B0 = 0.000769;
XAxis_CH->iir[2].B1 = 0.001538;
XAxis_CH->iir[2].B2 = 0.000769;
XAxis_CH->iir[2].A1 = 1.92076;
XAxis_CH->iir[2].A2 = -0.923833;
///////////////////////////////////////// Y Axis Master configration ////////////////////////////////////////////
YAxis_MASTER_CH->InputMode = NO_INPUT_MODE;
YAxis_MASTER_CH->OutputMode = STEP_DIR_MODE;
YAxis_MASTER_CH->Vel = Velocity;
YAxis_MASTER_CH->Accel = 200000;
YAxis_MASTER_CH->Jerk = 4e+006;
YAxis_MASTER_CH->P = 0;
YAxis_MASTER_CH->I = 0.01;
YAxis_MASTER_CH->D = 0;
YAxis_MASTER_CH->FFAccel = 0;
YAxis_MASTER_CH->FFVel = 0;
YAxis_MASTER_CH->MaxI = 200;
YAxis_MASTER_CH->MaxErr = 1e+006;
YAxis_MASTER_CH->MaxOutput = 200;
YAxis_MASTER_CH->DeadBandGain = 1;
YAxis_MASTER_CH->DeadBandRange = 0;
YAxis_MASTER_CH->InputChan0 = 0;
YAxis_MASTER_CH->InputChan1 = 0;
YAxis_MASTER_CH->OutputChan0 = YMas_OutputCh; //
YAxis_MASTER_CH->OutputChan1 = 0;
YAxis_MASTER_CH->MasterAxis = -1;
//YAxis_MASTER_CH->LimitSwitchOptions=0x0;
YAxis_MASTER_CH->LimitSwitchOptions = 0x00; //115 105
YAxis_MASTER_CH->LimitSwitchNegBit = YMas_Lim;
YAxis_MASTER_CH->LimitSwitchPosBit = YMas_Lim;
YAxis_MASTER_CH->SoftLimitPos = 1e+009;
YAxis_MASTER_CH->SoftLimitNeg = -1e+009;
YAxis_MASTER_CH->InputGain0 = 1;
YAxis_MASTER_CH->InputGain1 = 1;
YAxis_MASTER_CH->InputOffset0 = 0;
YAxis_MASTER_CH->InputOffset1 = 0;
YAxis_MASTER_CH->OutputGain = 1;
YAxis_MASTER_CH->OutputOffset = 0;
YAxis_MASTER_CH->SlaveGain = 1;
YAxis_MASTER_CH->BacklashMode = BACKLASH_OFF;
YAxis_MASTER_CH->BacklashAmount = 0;
YAxis_MASTER_CH->BacklashRate = 0;
YAxis_MASTER_CH->invDistPerCycle = 1;
YAxis_MASTER_CH->Lead = 0;
YAxis_MASTER_CH->MaxFollowingError = 1000000000;
YAxis_MASTER_CH->StepperAmplitude = 20;
YAxis_MASTER_CH->iir[0].B0 = 1;
YAxis_MASTER_CH->iir[0].B1 = 0;
YAxis_MASTER_CH->iir[0].B2 = 0;
YAxis_MASTER_CH->iir[0].A1 = 0;
YAxis_MASTER_CH->iir[0].A2 = 0;
YAxis_MASTER_CH->iir[1].B0 = 1;
YAxis_MASTER_CH->iir[1].B1 = 0;
YAxis_MASTER_CH->iir[1].B2 = 0;
YAxis_MASTER_CH->iir[1].A1 = 0;
YAxis_MASTER_CH->iir[1].A2 = 0;
YAxis_MASTER_CH->iir[2].B0 = 0.000769;
YAxis_MASTER_CH->iir[2].B1 = 0.001538;
YAxis_MASTER_CH->iir[2].B2 = 0.000769;
YAxis_MASTER_CH->iir[2].A1 = 1.92076;
YAxis_MASTER_CH->iir[2].A2 = -0.923833;
////////////////////////////////////////// Y Axis Slave configration///////////////////////////////////////////////////////////
YAxis_SLAVE_CH->InputMode = NO_INPUT_MODE;
YAxis_SLAVE_CH->OutputMode = STEP_DIR_MODE;
YAxis_SLAVE_CH->Vel = Velocity;
YAxis_SLAVE_CH->Accel = 200000;
YAxis_SLAVE_CH->Jerk = 4e+006;
YAxis_SLAVE_CH->P = 0;
YAxis_SLAVE_CH->I = 0.01;
YAxis_SLAVE_CH->D = 0;
YAxis_SLAVE_CH->FFAccel = 0;
YAxis_SLAVE_CH->FFVel = 0;
YAxis_SLAVE_CH->MaxI = 200;
YAxis_SLAVE_CH->MaxErr = 1e+006;
YAxis_SLAVE_CH->MaxOutput = 200;
YAxis_SLAVE_CH->DeadBandGain = 1;
YAxis_SLAVE_CH->DeadBandRange = 0;
YAxis_SLAVE_CH->InputChan0 = 0;
YAxis_SLAVE_CH->InputChan1 = 0;
YAxis_SLAVE_CH->OutputChan0 = YSla_OutputCh; //
YAxis_SLAVE_CH->OutputChan1 = 0;
YAxis_SLAVE_CH->MasterAxis = YMasAxis;
//YAxis_SLAVE_CH->LimitSwitchOptions=0x0;
YAxis_SLAVE_CH->LimitSwitchOptions = 0x00; //115 105
YAxis_SLAVE_CH->LimitSwitchNegBit = YSla_Lim;
YAxis_SLAVE_CH->LimitSwitchPosBit = YSla_Lim;
YAxis_SLAVE_CH->SoftLimitPos = 1e+009;
YAxis_SLAVE_CH->SoftLimitNeg = -1e+009;
YAxis_SLAVE_CH->InputGain0 = 1;
YAxis_SLAVE_CH->InputGain1 = 1;
YAxis_SLAVE_CH->InputOffset0 = 0;
YAxis_SLAVE_CH->InputOffset1 = 0;
YAxis_SLAVE_CH->OutputGain = 1;
YAxis_SLAVE_CH->OutputOffset = 0;
YAxis_SLAVE_CH->SlaveGain = 1;
YAxis_SLAVE_CH->BacklashMode = BACKLASH_OFF;
YAxis_SLAVE_CH->BacklashAmount = 0;
YAxis_SLAVE_CH->BacklashRate = 0;
YAxis_SLAVE_CH->invDistPerCycle = 1;
YAxis_SLAVE_CH->Lead = 0;
YAxis_SLAVE_CH->MaxFollowingError = 1000000000;
YAxis_SLAVE_CH->StepperAmplitude = 20;
YAxis_SLAVE_CH->iir[0].B0 = 1;
YAxis_SLAVE_CH->iir[0].B1 = 0;
YAxis_SLAVE_CH->iir[0].B2 = 0;
YAxis_SLAVE_CH->iir[0].A1 = 0;
YAxis_SLAVE_CH->iir[0].A2 = 0;
YAxis_SLAVE_CH->iir[1].B0 = 1;
YAxis_SLAVE_CH->iir[1].B1 = 0;
YAxis_SLAVE_CH->iir[1].B2 = 0;
YAxis_SLAVE_CH->iir[1].A1 = 0;
YAxis_SLAVE_CH->iir[1].A2 = 0;
YAxis_SLAVE_CH->iir[2].B0 = 0.000769;
YAxis_SLAVE_CH->iir[2].B1 = 0.001538;
YAxis_SLAVE_CH->iir[2].B2 = 0.000769;
YAxis_SLAVE_CH->iir[2].A1 = 1.92076;
YAxis_SLAVE_CH->iir[2].A2 = -0.923833;
////////////////////////////////////////// Z Axis Master configration ////////////////////////////////////////////
ZAxis_MASTER_CH->InputMode = NO_INPUT_MODE;
ZAxis_MASTER_CH->OutputMode = STEP_DIR_MODE;
ZAxis_MASTER_CH->Vel = Velocity;
ZAxis_MASTER_CH->Accel = 200000;
ZAxis_MASTER_CH->Jerk = 4e+006;
ZAxis_MASTER_CH->P = 0;
ZAxis_MASTER_CH->I = 0.01;
ZAxis_MASTER_CH->D = 0;
ZAxis_MASTER_CH->FFAccel = 0;
ZAxis_MASTER_CH->FFVel = 0;
ZAxis_MASTER_CH->MaxI = 200;
ZAxis_MASTER_CH->MaxErr = 1e+006;
ZAxis_MASTER_CH->MaxOutput = 200;
ZAxis_MASTER_CH->DeadBandGain = 1;
ZAxis_MASTER_CH->DeadBandRange = 0;
ZAxis_MASTER_CH->InputChan0 = 0;
ZAxis_MASTER_CH->InputChan1 = 0;
ZAxis_MASTER_CH->OutputChan0 = ZMas_OutputCh; //
ZAxis_MASTER_CH->OutputChan1 = 0;
ZAxis_MASTER_CH->MasterAxis = -1;
//ZAxis_MASTER_CH->LimitSwitchOptions=0x0;
ZAxis_MASTER_CH->LimitSwitchOptions = 0x00; //115 105
ZAxis_MASTER_CH->LimitSwitchNegBit = ZMas_Lim;
ZAxis_MASTER_CH->LimitSwitchPosBit = ZMas_Lim;
ZAxis_MASTER_CH->SoftLimitPos = 1e+009;
ZAxis_MASTER_CH->SoftLimitNeg = -1e+009;
ZAxis_MASTER_CH->InputGain0 = 1;
ZAxis_MASTER_CH->InputGain1 = 1;
ZAxis_MASTER_CH->InputOffset0 = 0;
ZAxis_MASTER_CH->InputOffset1 = 0;
ZAxis_MASTER_CH->OutputGain = 1;
ZAxis_MASTER_CH->OutputOffset = 0;
ZAxis_MASTER_CH->SlaveGain = 1;
ZAxis_MASTER_CH->BacklashMode = BACKLASH_OFF;
ZAxis_MASTER_CH->BacklashAmount = 0;
ZAxis_MASTER_CH->BacklashRate = 0;
ZAxis_MASTER_CH->invDistPerCycle = 1;
ZAxis_MASTER_CH->Lead = 0;
ZAxis_MASTER_CH->MaxFollowingError = 1000000000;
ZAxis_MASTER_CH->StepperAmplitude = 20;
ZAxis_MASTER_CH->iir[0].B0 = 1;
ZAxis_MASTER_CH->iir[0].B1 = 0;
ZAxis_MASTER_CH->iir[0].B2 = 0;
ZAxis_MASTER_CH->iir[0].A1 = 0;
ZAxis_MASTER_CH->iir[0].A2 = 0;
ZAxis_MASTER_CH->iir[1].B0 = 1;
ZAxis_MASTER_CH->iir[1].B1 = 0;
ZAxis_MASTER_CH->iir[1].B2 = 0;
ZAxis_MASTER_CH->iir[1].A1 = 0;
ZAxis_MASTER_CH->iir[1].A2 = 0;
ZAxis_MASTER_CH->iir[2].B0 = 0.000769;
ZAxis_MASTER_CH->iir[2].B1 = 0.001538;
ZAxis_MASTER_CH->iir[2].B2 = 0.000769;
ZAxis_MASTER_CH->iir[2].A1 = 1.92076;
ZAxis_MASTER_CH->iir[2].A2 = -0.923833;
////////////////////////////////////////// Z Axis Slave connfigration/ //////////////////////////////////////////////////////////
ZAxis_SLAVE_CH->InputMode = NO_INPUT_MODE;
ZAxis_SLAVE_CH->OutputMode = STEP_DIR_MODE;
ZAxis_SLAVE_CH->Vel = Velocity;
ZAxis_SLAVE_CH->Accel = 200000;
ZAxis_SLAVE_CH->Jerk = 4e+006;
ZAxis_SLAVE_CH->P = 0;
ZAxis_SLAVE_CH->I = 0.01;
ZAxis_SLAVE_CH->D = 0;
ZAxis_SLAVE_CH->FFAccel = 0;
ZAxis_SLAVE_CH->FFVel = 0;
ZAxis_SLAVE_CH->MaxI = 200;
ZAxis_SLAVE_CH->MaxErr = 1e+006;
ZAxis_SLAVE_CH->MaxOutput = 200;
ZAxis_SLAVE_CH->DeadBandGain = 1;
ZAxis_SLAVE_CH->DeadBandRange = 0;
ZAxis_SLAVE_CH->InputChan0 = 0;
ZAxis_SLAVE_CH->InputChan1 = 0;
ZAxis_SLAVE_CH->OutputChan0 = ZSla_OutputCh; //
ZAxis_SLAVE_CH->OutputChan1 = 0;
ZAxis_SLAVE_CH->MasterAxis = ZMasAxis;
//ZAxis_SLAVE_CH->LimitSwitchOptions=0x0;
ZAxis_SLAVE_CH->LimitSwitchOptions = 0x00; //115 105
ZAxis_SLAVE_CH->LimitSwitchNegBit = ZSla_Lim;
ZAxis_SLAVE_CH->LimitSwitchPosBit = ZSla_Lim;
ZAxis_SLAVE_CH->SoftLimitPos = 1e+009;
ZAxis_SLAVE_CH->SoftLimitNeg = -1e+009;
ZAxis_SLAVE_CH->InputGain0 = 1;
ZAxis_SLAVE_CH->InputGain1 = 1;
ZAxis_SLAVE_CH->InputOffset0 = 0;
ZAxis_SLAVE_CH->InputOffset1 = 0;
ZAxis_SLAVE_CH->OutputGain = 1;
ZAxis_SLAVE_CH->OutputOffset = 0;
ZAxis_SLAVE_CH->SlaveGain = 1;
ZAxis_SLAVE_CH->BacklashMode = BACKLASH_OFF;
ZAxis_SLAVE_CH->BacklashAmount = 0;
ZAxis_SLAVE_CH->BacklashRate = 0;
ZAxis_SLAVE_CH->invDistPerCycle = 1;
ZAxis_SLAVE_CH->Lead = 0;
ZAxis_SLAVE_CH->MaxFollowingError = 1000000000;
ZAxis_SLAVE_CH->StepperAmplitude = 20;
ZAxis_SLAVE_CH->iir[0].B0 = 1;
ZAxis_SLAVE_CH->iir[0].B1 = 0;
ZAxis_SLAVE_CH->iir[0].B2 = 0;
ZAxis_SLAVE_CH->iir[0].A1 = 0;
ZAxis_SLAVE_CH->iir[0].A2 = 0;
ZAxis_SLAVE_CH->iir[1].B0 = 1;
ZAxis_SLAVE_CH->iir[1].B1 = 0;
ZAxis_SLAVE_CH->iir[1].B2 = 0;
ZAxis_SLAVE_CH->iir[1].A1 = 0;
ZAxis_SLAVE_CH->iir[1].A2 = 0;
ZAxis_SLAVE_CH->iir[2].B0 = 0.000769;
ZAxis_SLAVE_CH->iir[2].B1 = 0.001538;
ZAxis_SLAVE_CH->iir[2].B2 = 0.000769;
ZAxis_SLAVE_CH->iir[2].A1 = 1.92076;
ZAxis_SLAVE_CH->iir[2].A2 = -0.923833;
EnableAxisDest(XAxis, 0); // 使能X轴通道
EnableAxisDest(YMasAxis, 0); // 使能Y主通道
EnableAxisDest(YSlaAxis, 0); // 使能Y从轴通道
EnableAxisDest(ZMasAxis, 0); // 使能Z主通道
EnableAxisDest(ZSlaAxis, 0); // 使能Z从轴通道
// DisableAxis(0);
DefineCoordSystem(XAxis, YMasAxis, ZMasAxis, -1); // 设置x,y,z轴对应的通道
SetBitDirection(X_Relay, 1); // 设置Relay 1对应的端口为输出模式
ClearBit(X_Relay); // 置0,代表松闸
SetBitDirection(Y_Relay, 1); // 设置Relay 1对应的端口为输出模式
ClearBit(Y_Relay); // 置0,代表松闸
SetBitDirection(Z_Relay, 1); // 设置Relay 1对应的端口为输出模式
ClearBit(Z_Relay); // 置0,代表松闸
Delay_sec(2); //松闸需要时间
SetBitDirection(45, 1); // set the Enable pin of the KFlop to be output mode
SetBit(45); // Make the Enable signal of the kFlop to be 1
printf("3Axis Configuration Completed::\n");
DisableAxis(XAxis); //
DisableAxis(YMasAxis); //
DisableAxis(YSlaAxis); //
DisableAxis(ZMasAxis); //
DisableAxis(ZSlaAxis); //
Zero(XAxis);
Zero(YMasAxis);
Zero(YSlaAxis);
Zero(ZMasAxis);
Zero(ZSlaAxis);
EnableAxis(XAxis); //
EnableAxis(YMasAxis); //
EnableAxis(YSlaAxis); //
EnableAxis(ZMasAxis); //
EnableAxis(ZSlaAxis); // */
XAxis_CH->LimitSwitchOptions = LimActOption;
YAxis_MASTER_CH->LimitSwitchOptions = LimActOption;
YAxis_SLAVE_CH->LimitSwitchOptions = LimActOption;
ZAxis_MASTER_CH->LimitSwitchOptions = LimActOption;
ZAxis_SLAVE_CH->LimitSwitchOptions = LimActOption;
Delay_sec(1);
// Assign soft limits to each channel
XAxis_CH->SoftLimitNeg = -700000.0;
XAxis_CH->SoftLimitPos = 700000.0;
YAxis_MASTER_CH->SoftLimitNeg = -300000;
YAxis_MASTER_CH->SoftLimitPos = 300000;
YAxis_SLAVE_CH->SoftLimitNeg = -300000;
YAxis_SLAVE_CH->SoftLimitPos = 300000;
ZAxis_MASTER_CH->SoftLimitNeg = -230000;
ZAxis_MASTER_CH->SoftLimitPos = 220000;
ZAxis_SLAVE_CH->SoftLimitNeg = -230000;
ZAxis_SLAVE_CH->SoftLimitPos = 220000;
#ifdef USEBRAKE //再松一次闸以防万一
ClearBit(Z_Relay);
Delay_sec(2); // 松闸需要时间
#endif
for (;;) // loop forever
// Dsiable axes if Estop is pressed
if (!ReadBit(ESTOP))
DisableAxis(XAxis); // axis still enabled? - Disable it
DisableAxis(YMasAxis); // axis still enabled? - Disable it
DisableAxis(YSlaAxis); // axis still enabled? - Disable it
DisableAxis(ZMasAxis); // axis still enabled? - Disable it
DisableAxis(ZSlaAxis); // axis still enabled? - Disable it
break;
// Service Amplifier disable after no activity for a while
if (XAxis_CH->Dest != LastX || YAxis_MASTER_CH->Dest != LastY || ZAxis_MASTER_CH->Dest != LastZ)
// we moved - enable KStep Amplifers
SetBit(45);
T0 = Time_sec(); // record the time and position of last motion
LastX = XAxis_CH->Dest;
LastY = YAxis_MASTER_CH->Dest;
LastZ = ZAxis_MASTER_CH->Dest;
if (Time_sec() > T0 + 60.0) ClearBit(45);
yethsts
Post by yethsts » Sat Aug 01, 2020 8:32 pm
Attachment is the Tools setting. I have changed the Cnts/Inch value of all x,y,z axis from 40000 to 20000. Things are slightly better, for example the XAxis_CH->SoftLimitPos must be larger than 1100000 before when Cnts/inci is 40000, but now needs only > 700000 for ok. But inner essence is the same.
yethsts
Post by yethsts » Sat Aug 01, 2020 8:39 pm
After initialization, I can use CNC's Jog button to drive the 5 motors moving. But can't run the example g code named DynoMotion.ngc. Awalys report: : "soft limit Y+ rapid tranverse job halted" or ": "soft limit X+ rapid tranverse job halted"."