JP8
JP8 provides all internal signal and power connections to KFLOP.This 16 pin ribbon connection should be as short as possible to avoid noise and crosstalk as the cable forms a high speed communication link.The Aux Bus supports multiple boards connected tot he same cable.In most case the specifics of the Aux Bus will be handled internally by KFLOP and no knowledge of the signals will be required for use.
The 8 data bits (DB0-DB7) are bi-directional.CLKIN and STARTIN allow a board to be selected by the address placed on the bus, and then a fixed sequence of 8-bit writes (2) and reads (5) can be performed using the CLKIN signal.
Pin KFLOP Name Konnect Name
1 VDD5 VDD5
2 VDD12 VDD12
3 VDD33 VDD33
4 RESET# RESET#
5 IO26 DB0
6 IO27 DB1
7 IO28 DB2
8 GND GND
9 GND GND
10 IO29 DB3
11 IO30 DB4
12 IO31 DB5
13 IO32 DB6
14 IO33 DB7
15 IO34 CLKIN
16 IO35 STARTIN
J2 Konnect Power
KonnectPower
The power signals from KFLOP's Aux Bus are available on the J2 terminals.It is not normally necessary to apply power to these terminals as power is supplied from KFLOP through the JP8 connector.For multiple boards it may be desirable to apply additional higher gauge power and GND connections between boards.Note the Signal labeled 12V is connected to the KFLOP 12V signal but may not be necessarily 12V.KFLOP and Konnect do not require or use the 12V signal but only pass the signal through the various connectors.Disk Drive Power Supplies usually supply +12V into KFLOP JR1 Pin 1.Also note that if any of these supply voltages are used for the Inputs or outputs then the Input wiring will not be isolated from KFLOP.
It is possible to supply +5V power to KFLOP through these terminals if the power consumption on KFLOP is less than 1 Amp and the ribbon cable connection is short (several inches or less).
Optically isolated Inputs
Individual Inputs
Individual Inputs (1 of 4 shown)
Input Bank Commons
Input Bank Commons
Konnect's 32 optically isolated inputs are grouped into 4 independent Banks of 8 inputs.This allows any Bank to be used with either sourcing or sinking signals.However all inputs in the same bank share the same common and must operate in the same mode. The 4 independent Banks also allow different supply voltages and supply isolation to be used for each Bank.24V is the preferred input voltage and will draw (24V - 1.4 - 1.4)/4K ~5ma of current.
Konnect's 32 optically isolated inputs can be driven from a +/- 4.75V to a +/-25V signal.Less than 2V should be applied to ensure the input is off.One of the 32 input circuits is shown below.The input consists of a AC type of Optocoupler in series with an LED indicator in series with a 4Kohm resistor.The AC type of input allows the common to be connected to either the Positive or Negative Supply voltage so that either sinking or sourcing outputs can be used (current can flow either direction to activate the input).
KonnectInputCircuit
External Wiring would typically be arranged such as:
CommonAnode
Opto Isolated Outputs
Out 1
Outputs (1 of 4 shown)
Each of the 16 Optically Isolated Outputs is completely isolated with a + and - terminal.When active the output passes current from the + to - terminals much like a relay contact would.
The Outputs are capable of driving medium power devices such as relay coils. Loads up to 30V @ 250ma may be driven.
The internal Konnect Output Circuitry is shown below which converts a photo transistor output to darlington transistor output. The 220Ohm resistor allows the output have a low on voltage for low currents before the transistor turns on.This allows the output to drive low current circuits with a smaller on voltage(2ma @ < 0.6V).For example LVTTL/TTL inputs require less than 0.8V to guarantee a low input.At higher currents Q1 becomes active and keeps the on voltage drop below 0.9V at 0.25A. Switching 0.25A at 24V allows loads up to 6W to be driven.
OptoOutput
A typical wiring diagram driving 24V relays.Because of the less than 0.9V drop on the Konnect outputs the load will be driven with more than 23.1V.
RelaysKonnect
Board Address Selection Jumpers
AddressJumpers
The KFLOP's Auxiliary Port works as a Bus where multiple boards can be connected to the same Port.Each board has an address so it can be selected as active.For a single Konnect board in the system removing all Jumpers will configure the Konnect Board Address as zero.If multiple boards are to be used set each board to an unique address.
A0 A1 A2 Address
Removed Removed Removed 0
Installed Removed Removed 1
Removed Installed Removed 2
Installed Installed Removed 3
Removed Removed Installed 4
Installed Removed Installed 5
Removed Installed Installed 6
Installed Installed Installed 7
KFLOP can be configured to service each Konnect Board using the AddKonnect function.The first parameter is the board address. The second parameter is the address of where KFLOP should obtain data to send to Konnect's 16 Outputs.The 3rd Parameter the address of where KFLOP should place the data received from Konnects 32 Inputs.
In most cases the addresses will be KFLOP Virtual I/O bit locations.KFLOP has two sets of Virtual I/O Bits, standard and extended. The standard consists of 16 Bits in VirtualBits, and the Extended consist of 1024 Bits in VirtualBitsEx[32].
The code below configures KFLOP to service 4 Konnect Boards (192 IO bits):
	InitAux();
	AddKonnect(0,&VirtualBits,VirtualBitsEx);
		AddKonnect(1,VirtualBitsEx+1,VirtualBitsEx+2);
		AddKonnect(2,VirtualBitsEx+3,VirtualBitsEx+4);
		AddKonnect(3,VirtualBitsEx+5,VirtualBitsEx+6);
Board 0 has Output Bits mapped to 48-63 and Input Bits Mapped to 1024-1055
Board 1 has Output Bits mapped to 1056-1071 and Input Bits Mapped to 1088-1119
Board 2 has Output Bits mapped to 1120-1135 and Input Bits Mapped to 1152-1183
Board 3 has Output Bits mapped to 1184-1199 and Input Bits Mapped to 1216-1247
Typical IO Mapping for Standard Single Konnect
Outputs Virtual IO Number
0 48
1 49
2 50
3 51
4 52
5 53
6 54
7 55
8 56
9 57
10 58
11 59
12 60
13 61
14 62
15 63
Inputs Virtual IO Number
0 1024
1 1025
2 1026
3 1027
4 1028
5 1029
6 1030
7 1031
8 1032
9 1033
10 1034
11 1035
12 1036
13 1037
14 1038
15 1039
16 1040
17 1041
18 1042
19 1043
20 1044
21 1045
22 1046
23 1047
24 1048
25 1049
26 1050
27 1051
28 1052
29 1053
30 1054
31 1055